Re: Handling of ramps and DVs in DMC sub-controllers

[ Follow Ups ] [ Post Followup ] [ Control Consulting ] [ FAQ ]

Posted by Venky Venkataraman on April 30, 2003 at 08:40:31:

In Reply to: Re: Handling of ramps and DVs in DMC sub-controllers posted by Richard Hughes on April 23, 2003 at 08:25:36:

If a ramp is configured as psuedo ramp, it trips only the sub controller.

I know of APC engineers who have done this on some of their projects to get around the ramp problems.

Venky

:
: I believe that the reason that the whole controller shuts down is due to the point in the controller cycle at which the imbalance is detected.

: For example if a sub-controller detects that a critical variable has gone bad, it detects this during the input variable validation, before the LP is run

: But .. if a ramp is imbalanced this is not detected until the LP solution has completed and failed to "balance the ramp"
: If a single sub-controller was switched off this would require a second LP solution, with no guarantee that there is enough time for it to run

: So as a pragmatic solution the whole controller is switched off


:
: :